Control Joints & Barrier Wall

Question

Are the control joint recommendations the same for a single wythe, fully grouted barrier wall, as they are for other CMU wall systems?  Would the control joints themselves be different?

Share this post


Link to post
Share on other sites

1 answer to this question

  • 0

The empirical layout and detailing recommendations of NCMA TEK 10-2C are applicable regardless of whether the CMU assembly is hollow, partially grouted, or fully grouted. If the assembly is solidly grouted because the reinforcement is closely spaced together (e.g., 8 or 16 inches on center vertical/horizontal) then it may also be worth considering the alternative crack control recommendations of TEK 10-3, which provide for an option to remove control joints altogether due to the presence of a large amount of reinforcing steel. Removing the control joints, however, does depend on the wall thickness, percentage of grouting, and reinforcement size and spacing.